richard reynolds July 31st 03 04:17 AM

Grounding Probe
 
Is it glass tank?
yes

The only way to eliminate this heater from the picture is completely
remove it from the AC outlet. Assumtion it does not flicker because
water is hotter than the thermostate setup is probably true, but it
does not say if we have current leak from it to water or not...
It could leak even if the thermostate does not turn it on. It could be
one pole switch, so one pole can be constantly on.


sorry didnt give enough details, the heater isnt leaking ive checked it a number of times,
both removal from E supply and total removal from tank, my reference to flickering is the
tank temp must be slightly colder than a normal reef, and its outside in SoCal it rained
today and the low is probibly 80F, i was just providing as much detail as i could and
missed a step.


I would be very surprised if you measured the same stray voltages
with different types of meters :-) Their readins will mostly depend
on their internal resistance compared to the resistance of the devices
insulation.


i used at least 4, 1 is analog and a tad old late '80s, 2 of which are crappy digitals
well $$$ kinda crappy but not analog or $2500 digitals either, the tectronics is a good
ociliscope with a V probe and one of them tectronics isolators(forgot what its called)
plug probe into it so you dont screw up scope when messing with things


Right... and since I am not a ray expert I have no idea what was
stressing your fish. In terms of electicity in other hand, I know
what I am saying... :-)


I just like the blue spot he is cool (actually think its a she but not 100% sure)

No, if everything is working - do not change anything... :-)
I would be only interested in two things:
- what is the influence of you heater being off to the stray voltages
- what is the reading of stray voltages from a set of different meters :-)


ive done it w/o the heater when I was trying to isolate the issue, as for the readings
ill either have to re take them or search around for the last time i posted them.

Good. I have no doubt your grounding is good.

BTW - do you have pictures of your outside tank setup?
I am interested in seeing it if you have them available.


i can make them available, but i was serious its covered in algae :(

--
richard reynolds






Marc Levenson July 31st 03 05:14 AM

Grounding Probe
 


Pszemol wrote:

Yes, it would, using your body grounded to the floor as a conductor.
How is a GFCI working in your bathroom without "grounding probe"? :-)
How is a GFCI on your hair-dryer working without a probe? :-)


Actually, the GCFI (I believe that is the correct order of initials) is grounded when
it is wired into the wall.

And I believe I read that 10mA trips it.

Marc

--
Personal Page: http://www.sparklingfloorservice.com/oanda/index.html
Business Page: http://www.sparklingfloorservice.com
Marine Hobbyist: http://www.melevsreef.com



richard reynolds July 31st 03 06:50 AM

Grounding Probe
 
Marc Levenson wrote in message ...
Yes, it would, using your body grounded to the floor as a conductor.
How is a GFCI working in your bathroom without "grounding probe"? :-)
How is a GFCI on your hair-dryer working without a probe? :-)


Actually, the GCFI (I believe that is the correct order of initials)


both gfci and gcfi are pointing to the same gfi or electronics device that seperates the
supply from the devices when a ground fault is found. ANSI calls it a GFCI so if one were
to argue there one of the ones setting the standards so they are correct :|

ive seen both used though, so is a mandarin goby correct really it is because its the
'common name' not meaining much when it comes to its scientific name which neither has
mandarin or goby in it. same aplies here

is grounded when it is wired into the wall.


your missing a step but thats ok
the devices ground means little (not nothing) it really has little to do with "ground" as
a third wire,
in easy terms it compars what is going to a device from what is coming back, if there
different it trips
in electronics if there is a difference then some current is going to ground and its
called a ground fault, it wont trip if there is a short, because the current going out the
supply and coming back on the return will be the same, even if its too much current it
doesnt know the difference.

And I believe I read that 10mA trips it.


you can buy these in more and less sensitive models depending on there use.


Marc

--
Personal Page: http://www.sparklingfloorservice.com/oanda/index.html
Business Page: http://www.sparklingfloorservice.com
Marine Hobbyist: http://www.melevsreef.com

--
richard reynolds





Pszemol July 31st 03 04:42 PM

Grounding Probe ( something to read guys)
 
"Boomer" wrote in message ...
No Marc and after more than 10 years even the electrical wizards (which I am not) are
still arguing. I don't think anyone has a real answer as it really hasn't been tested as
far as I'm concerned, I just hear statements and no data. Fact of the matter is, that even
with GFIC's there is still "Induced Voltage" in the water in aquariums and I don't mean
"stray voltage" witch is another issue. Any electrical device in or even near an aquarium
will induce voltage into the water, it has been measured 100's of times. Power cords,
cables, heaters, etc., all generate an electrical field in water, which can be measured.
An Amp Clamp is an electrical device electricians use to measure amps, you don't connect
anything to it, the wire in question is just placed in the "C' like ring and the number of
amp's is directly proportional to the induced field the cord generates. You also don't
need to plug in a fluorescent light bulb in either, if you are close enough to a high
tension power line, the generated fields by themselves will light the bulb.


Right. But there is no way to shield every electric device or wires in the walls
to get rid of this electric noise in our modern society... You would have to get
rid of TV-sets, computers, electric pumps&motors, lights definetely and you will
still not recreate conditions similar to what is in the ocean, couple of miles from
the shore, couple hundred meters deep :-) Also, we have to remember about the dualism
of the electric energy becoming magnetic energy and vice versa... Every single change
in an electric field will cause a change in magnetic field so the water as a conductor,
grounded or not, will never be quiet in electro-magnetic terms as long as there is
a source of electromagnetic noise near by. There is no ways to recreate ocean in 100%
and grounding probe does not really help here much.

BTW - Amp Clamp is working simply as transformer or Hal sensor. In the first
case it just measure current flowing in the wire, not induced voltage...

All public
aquariums with shark tanks have the water grounded, with a probe, to eliminate any stray
or induced voltage, as Elasmobranches have what is called a Lorenzini Organ, which can
detect, in seawater, 0.005 uV or 5nV / cm @ 0.33 meters.


I just wonder what kind of current has to flow in the seawater to generate
such voltage difference...

You will never find a piece of
the ocean that generates say 18 V induced, but a power head may/will. If it is not in the
ocean it should not be in a tank. I am not questioning the stray voltage issue, just the
induced voltage issue, they are not the same. All of which means, IMHO, that a GFIC w/
probe or a GFIC / without a probe doesn't solve the two problems. Maybe someone can
invent, just for us, a GFIC which also eliminates any Induced Voltage, without the
potential side effect of a GFIC with a probe


The voltage is always measured between two points. So when you are talking about
powerhead induced voltage, lets say 18V, are refering to what two points?
To the ground? Or two points in different places inside tank?
In the first case - fish does not care about voltages relative to the ground
unless it does have contact with this ground. Similarly like birds on 20kV wire.

Pszemol

It is rather odd that you disagree with Gerry Parker but agree with Robert Michelson,
when Michelson states

"A reference on the web for empirical data on aquarium voltage and current is"
http://www.aquarium.net/1298/1298_3.shtml , which is Gerry's article.


Garry did not make mistake in using scope and collecting data from it.
He has measured different things correctly... He made a big mistake
interpreting collected data - thats all :-) When you wear a wool sweter
there are thousands volts generated and you can often feel a spark.
Should I be affraid touching wool sweter in the same way I should be
affraid touching 20kV coming out from the electric plant? :-)
It looks to me the science behind voltages, amperes, ohms is kind of
fuzzy for Garry and his "educated folks". But it is only my observation.
You do not have to agree with me, of course :-)

I think Gerry
pretty much know his P & Q 's and knows how and what he is measuring


I do not know Garry, so I cannot tell you who is he, but obviously he must
be also scared like hell when he is elevated at the Observation Deck in
any tower like Hancock, Sears in Chicago. I am affraid to jump, but I am
fine with standing there :-))

Pszemol July 31st 03 04:51 PM

Grounding Probe
 
"Boomer" wrote in message ...
http://www-training.llnl.gov/trainin...GFCIworks.html

http://www.howstuffworks.com/question117.htm


Good idea of posting such info - it will help folks not familiar
very much with electricity understand this discussion better...

Also, I can verify I was understanding correctly how it works,
so people jumping so quickly to correct me, or call a troll,
have a chance now to correct themselves :-)

richard reynolds July 31st 03 05:43 PM

Grounding Probe ( something to read guys)
 
huge snip
as Elasmobranches have what is called a Lorenzini Organ, which can
detect, in seawater, 0.005 uV or 5nV / cm @ 0.33 meters.


thanks was inches from looking the name of that organ up

another huge snip

--
Boomer

--
richard reynolds





J August 1st 03 05:04 AM

Grounding Probe ( something to read guys)
 
Thank you boomer for finally setting people on the right road.
Some here say a GFCI doesn't need a ground. I'm like thats how it works it
needs the ground.
ohh well have fun arguing with people here.

"Boomer" wrote in message
...
Pszemol

Just for you, this should make you happy :-)

"Ok. I finally did it. I finally figured out the whole mystery of stray
voltages
in a tank. I'll explain it, but first a disclaimer:

All tanks should have a ground probe and a GFI socket. Parts of this
document talk about doing unorthodox things to outlets and ground
probes-- which fall under the category of "Kids, don't do this at home".

Other parts talk imply that ground probes are not all that good, while
is arguably true for your fish, it is not true for YOU. Don't risk
death.
Use a ground probe and GFI socket. Your tank is not worth your
life. We now return to our regularly scheduled program...


It happens all the time. Someone takes a multimeter and measures
the voltage between their water and earth ground. They get 30 to
60 volts and then panic, thinking that this is somehow bad and that
they should do something to get rid of it. They then post a question
on the net and they get dozens of answers saying the same thing,
"The stray voltage is caused by electrical induction with your pumps.
Use a ground probe to get rid of it".

Sometimes, this stray voltage is fingered as the cause to fish stress,
Head and Lateral Line Erosion (HLLE), and other mysterious fish
deaths.

I'll cut to the chase here and say that both of these are incorrect.
Induction is not the cause of stray voltages. Ground probes are
not going to remove it. And it cannot possibly be the cause of
fish deaths. I can't imagine how these myths got started, especially
since it is very easy for someone to find the true cause of
stray voltages.

The true source of the stray voltages is capacitive coupling,
not inductive coupling and not resistive. Ground probes (or a
multimeter) actually complete the circuit for electricity to flow.
Since electricity doesn't flow unless the circuit is completed,
electricity won't be flowing in a tank without a ground probe.
Therefore, mysterious fish deaths in tanks without a ground
probe cannot be attributed to stray voltages since current is
not flowing in the tank to begin with.

I'm about to go into a long, technical explanation for the cause
of stray voltages. If you don't want to read it, you can stop
here. I've said/typed all the important practical information
already. I realize that what I'm saying goes against decades of
common misbelief so some proof is required. What follows
is the proof.

For the proof, I assume that you know basic electricity. Ohms
law, resistor dividers, and the general properties of transformers,
capacitors, and inductors. You don't need a great deal of this
knowledge, but enough so that you can picture what's going
on since there are no pictures in this post.

To find the source of this stray voltage, we must eliminate sources
that don't fit the evidence. Possible sources are induction, resistive
coupling, and capacitive coupling. There are other possible sources,
but the odds of these being the cause are so remote that we can ignore
them.

Here is the evidence that can be easily measured:
o The "stray voltage" changes (and is repeatable) depending on what

is turned on-- including the lights.
o If you put a resistor between the ground probe and earth ground,
and measure the current through the resistor, you will measure
up to about 40 uA. The voltage across the resistor will depend

on the value of the resistor, according to ohms law.
o The stray voltage/current does not change with the position of
the ground probe.
o The voltage measured between two ground probes is zero,
regardless of their position or orientation.
o If you disconnect the NEUTRAL line to the pumps/lights/etc. while
leaving
HOT connected, the stray voltage almost DOUBLES!
o The resistance, as measured by my multimeter, between the ground
probe and neutral/hot of the pumps/lights/etc. is infinite
(I.E., open).

Let's start with induction, since that is the common myth. If this
were happening, then electrically the tank would look like a
transformer.
The wiring in the pumps/heaters/lights would work like the primary
coil of the transformer. The water itself would be the secondary coil.

Unfortunately, the evidence does not support the induction theory.
In a transformer, if current is not flowing in the primary then no
current
will flow in the secondary. If induction were the cause then
disconnecting
HOT would cause the stray voltage to go to zero, not double. If
induction
were the cause, then almost zero current would flow through the ground
probe but we have 40 uA. If induction were the cause, then moving the
ground probe around the tank, or using two ground probes, would give
us different results. Conclusion: It's not induction!

So that leaves resistive coupling, or capacitive coupling.

Electrically, resistive coupling would look like a voltage divider. One

resistor of the divider would be the insulation (or lack there of)
surrounding the pumps. The other resistor would be the multimeter
itself, the ground probe, or a real resistor that we put in.

You can actually calculate the "resistance" of the insulation using
ohms law. Let's assume that we have 25 uA of current flowing.
Using ohms law then X ohms = 120 volts / 0.000025 Amps, or
4.8 Meg ohms. My multimeter is calibrated for up to 40.0 ohms,
so it should be able to measure this without problems. But since
it measured as an open circuit, they resistance theory can't be
correct.

Two notes about resistance... You'll notice that I didn't take
into account the resistance of the water or the resistor that I used
to make the current measurements. That's because those things
have much less resistance than the estimated 4.8 meg ohms. It
was a shortcut for sure, but the resistance of the water and
resistor was less than 100 kohms, or about 2% of the total
resistance.


Also... The way most people measure the stray voltage is by
placing the multimeter between the tank and earth ground.
In this case, the multimeter itself acts as one resistor in the
voltage divider. The multimeter has a high, but finite,
resistance. That's why I used a separate resistor
between the ground probe and earth ground, and measured
the voltage across this resistor. The resistor was anywhere
from 100 to 100k ohms. When you have a two resistors in
parallel, one of low value and the other of high value, the low
value resistor will be dominant. The high value resistor (the
multimeter) will not play a huge electrical role and mess up
the measured values. In this way, I could be assured that my
measurements were correct.

With capacitive coupling, you must know that a capacitor
can behave like a resistor when an AC current is applied to
it. The resistance is proportional to, and increases with,
frequency. The formula for calculating the resistance at
a given frequency is: Resistance = 1 / (2 * Pi * Freq * Cap),
where resistance is in ohms, freq is in Hz, and Cap is in Farads.

So, with capacitive coupling is set up exactly like the resistive
coupling above but with a cap as the electrical link between
the AC Mains and the water. If we expect to see a 4.8 meg ohm
resistor, then we can use the above formula to find the expected
capacitance. So... 4.8 meg Ohms = 1 / (2 * Pi * 60 * Cap).
Solving for Cap gives us 552 pF.

My multimeter will measure capacitance, but it isn't calibrated
into the 1000 pF range. So I expected some "not quite right numbers".
I measured the capacitance between the ground probe and hot or
neutral at around 1100 pF. This was suprising, since I didn't expect
the numbers to be that far off. That's when I did the "disconnect
neutral and leave hot connected" experiment. In this experiment the
stray voltage doubled! Then the numbers made sense.

At 1100 pF, 60 Hz, and 25 uA, the resistance of the cap should be
about 2.4 meg ohms. This should cause double the current to flow
through our voltage divider, which causes our measured voltages to
be double. The evidence matches this perfectly when neutral is
disconnected.

With neutral connected, the AVERAGE VOLTAGE inside the pumps,
lights, etc. is exactly half of the 120 volts applied to it. That's
because
of the voltage drop from the current flowing through it. When we
disconnect neutral, there is no current flowing so there is no voltage
drop. When there is no current running through the pumps, then
the average voltage is 120 volts. This explains why the voltage
doubles/halves depending on the neutral connection.

So, now all the evidence points to capacitive coupling!

For capacitive coupling to work, a circuit must be formed.
This is normally done by a ground probe (or the multimeter).
If there is no circuit, then there cannot possibly be any current
flowing!

People claim that once they add the ground probe then they
cannot measure any more stray voltage-- thus the ground
probe must have removed it! This is, of course, not true.
Essentially, what's happening is they are measuring the
voltage drop across a zero ohm resistor (the ground probe).
And of course there will be no voltage drop across such a
resistor! That's why they claim that it went away.

Naturally, life is more complex than that. It's not a zero ohm
resistor, since you have to take into account the resistance of
the water and the proximity of everything. But generally
speaking, adding the ground probe will bring the measured
"stray voltage" very close to zero.

Conclusions:

1. Very Important! Use a ground probe and GFI for your safety.
2. "Stray Voltage" is caused by capacitive coupling, not induction.

3. There is nothing you can do about it, unless you don't use
electricity in your tanks (including lights).
4. A ground probe will cause, not prevent, current from flowing in
a tank.
5. The lack of current flowing has never been attributed to the
death
of anything (except the lack of the normal electrical impulses
in the brain and nervous system). So, ground probes cannot
possibly solve things like HLLE, fish stress, etc.


I hope that this removes a lot of the popular myths that have been
circulating for decades about stray voltages in our tanks!

David Kessner


"I've been employed as an electrical engineer for almost the last 20
years, and everything that David wrote is completely legit. The only

claim
that I can't back up is the one concerning whether electrical fields

and/or
currents can cause diseases in fish, but that's only becuase I don't know
much about the physiology of fish.."

Hans Lehmann


So the issue is still unsolved on whether fish are affected or not

I'm surew you will enjou all of this in this thread


http://groups.google.com/groups?hl=e...1eecc.16483120
%40NEWS.erols.

com&rnum=6&prev=/groups%3Fq%3Dskates%2Bgroup:rec.aquaria.marine.ree fs%26hl%3
Den%26lr%3D%26
ie%3DUTF-8%26selm%3D3601eecc.16483120%2540NEWS.erols.com%26 rnum%3D6









SG August 1st 03 05:39 AM

Grounding Probe ( something to read guys)
 
Boomer quoted Someone who wrote:

o The resistance, as measured by my multimeter, between the ground
probe and neutral/hot of the pumps/lights/etc. is infinite
(I.E., open).


This is odd. In North America the resistance between ground and
neutral should be zero as neutral is connected to ground at the power
panel. The resistance between hot and ground or neutral should be
infinite.


Let's start with induction, since that is the common myth.


The author claims there is no inductive coupling, but we know there
must be. When there is a moving magnetic field (from powerheads and
other pumps) there will be current flow. It may be correct to say that
the inductive coupling is minimal. The other paper supports this theory.


If induction were the cause, then moving the
ground probe around the tank, or using two ground probes, would give
us different results.


This I have serious problems with. I would like to see the theory that
supports the argument.


richard reynolds August 1st 03 06:17 AM

Grounding Probe ( something to read guys)
 
humm stiring up the mind

SG wrote in message ...
Boomer quoted Someone who wrote:

o The resistance, as measured by my multimeter, between the ground
probe and neutral/hot of the pumps/lights/etc. is infinite
(I.E., open).


This is odd. In North America the resistance between ground and
neutral should be zero as neutral is connected to ground at the power
panel. The resistance between hot and ground or neutral should be
infinite.


yea odd, is there a different way of isolating the neutral/ground/hot wires elseware i
know us US ppl can be odd sometimes.

Let's start with induction, since that is the common myth.


The author claims there is no inductive coupling, but we know there
must be. When there is a moving magnetic field (from powerheads and
other pumps) there will be current flow. It may be correct to say that
the inductive coupling is minimal. The other paper supports this theory.


an issue for me is, even with minimal remember my issue is i had a ****ed off ray :) what
you might say is minimal might be ****ing this ray off. capiable of picking up voltages
well below the meters, the scope does pick up things they wont, but even then the ray
might pick up even more, the people shock factor for me is seriously minimal no arms go in
this tank when anything is pluged in anyways and i dont have kids to stick there hands in
it.

If induction were the cause, then moving the
ground probe around the tank, or using two ground probes, would give
us different results.


This I have serious problems with. I would like to see the theory that
supports the argument.


I never thought that 2 ground probes would give a different result I have 2 1 in tank 1 in
sump interesting worthy of closer examination i didnt place the 2nd for any reason only
because i figured better safe than sorry

also the scope did show different values based on where in the tank the probe was
positioned maybee the meters used in his "test" were not capiable of the difference.

--
richard reynolds





richard reynolds August 1st 03 06:30 AM

Grounding Probe
 
Boomer wrote in message ...
LOL " mandarin goby" , yup I know what you mean Richard, but that fish has often been

put
in the wrong family by hobbyists, who 'think' it is Goby but actually is a Dragonet and
not a Goby


and whats up with that how stoned was the person that made the link between Callionymidae
and dragonet and "ray fined fishes"

--
Boomer


:) just some minor humor mixed in with minor facts :)
--
richard reynolds






All times are GMT +1. The time now is 05:10 AM.

Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
FishKeepingBanter.com