The same situation could happen in any other wet environment.
Such as fish tank: salt water spilled on the floor where you stand combined with a faulty electric device submersed in the water where you put your hands can be very deadly combination and that is the reason smart people recommend GFCI for us to power fish tanks equipment from. Right, Especially on concrete! (Giant solid gelatin).... But what about wood flooring or Carpet? The majority of aquarium devices do not include grounds in their cords. However they really should. A ground probe provides a positive ground to the tank to trip the GFCI immediately in case of a problem. It is just an added safety measure. However, like you I believe the other stuff is hocus pocus snake oil..... However, after saying that, imagine the fact that the entire tank essentially becomes a Faraday Cage once the ground it inserted. More physics than I would like to think about this early. I am sure that a book could be written about this subject if studied in a lab. Only then would such discussions be resolved. Until then this is just opinion versus opinion.... "Pszemol" wrote in message ... "Stephen" wrote in message ... GFCI's are installed in bathrooms and kitchens because you are literally surrounded by potential grounds. The plumbing system! Running Water! Metal Basins! etc... The same situation could happen in any other wet environment. Such as fish tank: salt water spilled on the floor wehre you stand combined with a faulty electric device submersed in the water where you put your hands can be very deadly combination and that is the reason smart people recommend GFCI for us to power fish tanks equipment from. You can hold an AC hot wire and not get shocked if you are not grounded.... Right. Is there anybody claiming anything else here? See my "birds sitting on a 20kV wire" example... :-) Not the name is GROUND FAULT CIRCUIT INTERRUPTER... You have to have a ground fault to trip the circuit interrupter.... I hope you do not derive all your knowledge about GFCI from its name ;-) I can easily imagine a scenario when GFCI will trip when grounding will be perfect and DO NOT trip when grounding is faulty... If your imagination does not work for some reason I can give you full description of such scenarios. Is then the GFCI name wrong? Let's change it! ;-) |
#22
|
|||
|
|||
![]()
"J" wrote in message news:guIVa.16583$YN5.16888@sccrnsc01...
He's a troll I believe. Are you sure you want to start childish name calling game? The answers to all his statements and questions are in my post but he won't listen or understand. In which of your posts are all the answers? |
#23
|
|||
|
|||
![]()
"Boomer" wrote in message ...
http://www.aquarium.net/1298/1298_3.shtml I read this before and I strongly disagree. Let me quote something terrible: "So if you now accept this as the normal case for SW tanks, you begin asking yourself if this is a problem. I have discussed this with several educated folks, and we have concluded that the minute currents in the tank, due to grounding with titanium probes, are much less significant than unterminated voltages on the order of tens or hundreds of volts" - this is totaly FALSE. And I have explained this already based on an example with standing on 10th floor and on the 2nd floor. Standing on the 10th floor (unterminated voltage) is not dangerous until you fall down (create a current flow). And by adding grounding probe to those detected stray voltages you are creating "minute currents" on the levels about 0.1-1mA even if all devices are in good order. I do not know Gerry Parker, but I can only say it is not enough to have an access to labolatory grade test equipment - you also have to know what are you exactly measuring. The test equipment unfortunately will not do the thinking part for you... http://avdil.gtri.gatech.edu/RCM/RCM...ingProbes.html This one, in oposite, is very good and convincing. "In conclusion, the addition of a "grounding probes" will guarantee an electrical current flow in your aquarium and may induce erratic behavior or disease in your fish. If you have defective aquarium appliances that are creating a current path in your aquarium by using the salt water as a conductive medium, then the solution is to repair the appliances or replace them... not divert a portion of the current into a "grounding probe"." This is exactly what I am trying to say here. "NO" to grounding probes - period. |
#24
|
|||
|
|||
![]()
"Stephen" wrote in message ...
Right, Especially on concrete! (Giant solid gelatin).... But what about wood flooring or Carpet? The majority of aquarium devices do not include grounds in their cords. However they really should. A ground probe provides a positive ground to the tank to trip the GFCI immediately in case of a problem. It is just an added safety measure. However, like you I believe the other stuff is hocus pocus snake oil..... This "added safety measure" is not needed. That is my point exactly. If there is no current flow enough to trip GFCI there is also not enough current flow to electrocute you. Do you agree on this matter? And, when you add grounding probe you are CAUSING current flows from a faulty device to the ground through the water column. GFCI are not designed to trip on current levels which stress your fish, so such currents can flow to the grounding probe unstopped. That is the reason I am strongly against the grounding probe as a cure to the faulty device leaking some electricity to the water. In the value range from 0-5mA GFCI will not react, so such currents as 5mA could flow from the faulty device to the ground with a help of this probe. However, after saying that, imagine the fact that the entire tank essentially becomes a Faraday Cage once the ground it inserted. I disagree. This is not a very good analogy. Situation in the fish tank is far more complicated. I would say that fish body resistance to the AC current is comparable to the salt water resistance so you cannot neglect currents flowing through the fish body in the calculation. The body of any living thing is full of electrolytes conducting electricity very well. More physics than I would like to think about this early. I am sure that a book could be written about this subject if studied in a lab. Only then would such discussions be resolved. Until then this is just opinion versus opinion.... I see you are not willing to challenge my scenarios with GFCI, ok :-) |
#25
|
|||
|
|||
![]()
feel free to tell me shut up if I'm pestering you..lol
Shut up! Heehe... Helping Marc to say it. He is just too nice to use those words. CapFusion,... |
#26
|
|||
|
|||
![]()
In article , Pszemol wrote:
"Boomer" wrote in message ... http://www.aquarium.net/1298/1298_3.shtml I read this before and I strongly disagree. Disagree all you want, but the paper is correct. The findings were based on scientific procedures and principles. http://avdil.gtri.gatech.edu/RCM/RCM...ingProbes.html This one, in oposite, is very good and convincing. It is convincing, but incorrect. The author did not do any research to arrive at their conclusions. If you have defective aquarium appliances that are creating a current path in your aquarium by using the salt water as a conductive medium, then the solution is to repair the appliances or replace them... not divert a portion of the current into a "grounding probe"." The grounding probe will cause the GFCI or circuit breaker to trip alerting you to the possibility of defective equipment. There will be currents flowing in an aquarium with or without the grounding probe. This is the nature of AC. |
#27
|
|||
|
|||
![]() "Pszemol" wrote in message ... "Stephen" wrote in message ... Right, Especially on concrete! (Giant solid gelatin).... But what about wood flooring or Carpet? The majority of aquarium devices do not include grounds in their cords. However they really should. A ground probe provides a positive ground to the tank to trip the GFCI immediately in case of a problem. It is just an added safety measure. However, like you I believe the other stuff is hocus pocus snake oil..... This "added safety measure" is not needed. That is my point exactly. If there is no current flow enough to trip GFCI there is also not enough current flow to electrocute you. Do you agree on this matter? I think you are confusing the functionality of a GFCI to a circuit breaker.... GFCI detects current leaking to ground, not the neutral wire... Without a ground, thats all there would be, current leaking to neutral.... And, when you add grounding probe you are CAUSING current flows from a faulty device to the ground through the water column. GFCI are not designed to trip on current levels which stress your fish, so such currents can flow to the grounding probe unstopped. That is the reason I am strongly against the grounding probe as a cure to the faulty device leaking some electricity to the water. In the value range from 0-5mA GFCI will not react, so such currents as 5mA could flow from the faulty device to the ground with a help of this probe. However, after saying that, imagine the fact that the entire tank essentially becomes a Faraday Cage once the ground it inserted. I disagree. This is not a very good analogy. Situation in the fish tank is far more complicated. I would say that fish body resistance to the AC current is comparable to the salt water resistance so you cannot neglect currents flowing through the fish body in the calculation. The body of any living thing is full of electrolytes conducting electricity very well. More physics than I would like to think about this early. I am sure that a book could be written about this subject if studied in a lab. Only then would such discussions be resolved. Until then this is just opinion versus opinion.... I see you are not willing to challenge my scenarios with GFCI, ok :-) |
#28
|
|||
|
|||
![]()
"Stephen" wrote in message ...
I think you are confusing the functionality of a GFCI to a circuit breaker.... GFCI detects current leaking to ground, not the neutral wire... Without a ground, thats all there would be, current leaking to neutral.... No, I am not confusing it. I fully understand how it works. And you are *almost* right saying it detects the current leaking to the ground wire. The exact statement is that GFCI detects a *difference* in the current value between hot and neutral wire. This difference can leak to the ground wire by the grounding probe *OR* through your hands, legs, the floor (or water pipes or gas line) then dirrectly to the ground. |
#29
|
|||
|
|||
![]()
"SG" wrote in message ...
In article , Pszemol wrote: This "added safety measure" is not needed. That is my point exactly. If there is no current flow enough to trip GFCI there is also not enough current flow to electrocute you. Do you agree on this matter? A GFCI will not trip unless a ground is present. Once a ground is present a GFCI takes some time to trip (but it is very fast). I want to be a ground for 120v for exactly zero seconds and no more. It is your choice :-) |
#30
|
|||
|
|||
![]()
"richard reynolds" wrote in message .. .
My goal is not to force you to change your mind. My goal was to express my opinion on this subject. It is up to each of us to make the best decision in order to care for animals we take our responsibility for. I know ! ![]() Good :-) there is some evidence but as i hinted to the study basically says we need to study it which isnt enough. Exactly :-) being a preditor tank the ONLY circulation is from the sump to tank (and back duh ![]() the sump is a 20long the tank is a 75 and completely covered in diatom algae ![]() the only thing in the tank is the ray, a porcupine puffer, a 4" very fine sand bed (forget dsb the ray tosses it over and over) and a ground probe (not the only one, not always in there) Is it glass tank? as its outside and as outside is easy to get to dirt to ground it instead of using the ground wire from the main i ran a seperate wire 10gague solid copper to a 10' grounding rod burried about 9' deep its all of 4' from the sump to the rod the box from the main has a circuit breaker plus one of them hard cutoff switches the breaker is a gfci breaker, this is attached to both ground probes and the canister heater one ground probe is in the sump the other is in the tank. the heaters grounded but I THINK that its only the outside thats really grounded not the part that touches the water when its working, ive tested this a few times and to the best i could come up with this is the case. I have 2 skimmers both americal typhoon's ran with rio 3500's with the rio rtv adapter YES IVE CHECKED THEM THERE NOT THE CAUSE figured id get that straight out because w/o it ppl are gona jump on these poor rios ![]() the return pump which ive checked out over and over is a slightly older little giant 3-md something there is a canister heater which probibly hasnt even flickerd sence april and a fan on a thermostat its ran on sence april ![]() The only way to eliminate this heater from the picture is completely remove it from the AC outlet. Assumtion it does not flicker because water is hotter than the thermostate setup is probably true, but it does not say if we have current leak from it to water or not... It could leak even if the thermostate does not turn it on. It could be one pole switch, so one pole can be constantly on. i get the same very very small stray voltage going through the probe What do you mean "voltage going through the probe"? I have already explained here a mistake people do measuring the voltage. You can prove me wrong by using very different voltmetter and measuring the voltage again. Tell me please what you have read from both readings. ill have to dig up details ive posted them before and while ive done it a few times, id like to not mess up the details. ive used analog and digital meters in several AC and DC modes, all good meters. I would be very surprised if you measured the same stray voltages with different types of meters :-) Their readins will mostly depend on their internal resistance compared to the resistance of the devices insulation. for all I can tell there is NOTHING in the tank adding to any current besides the tank/water/fish Tell me more how did you find out about this. trial and error and a few dead rays ![]() I should point out the "for all I can tell" part one more time. Right... and since I am not a ray expert I have no idea what was stressing your fish. In terms of electicity in other hand, I know what I am saying... :-) I am glad you are happy. But you can help others adding more details about your setup. Please do. ill be glad to do any tests you can think of in the interest in providing a better place ![]() but I'd like to not re do them all, No, if everything is working - do not change anything... :-) I would be only interested in two things: - what is the influence of you heater being off to the stray voltages - what is the reading of stray voltages from a set of different meters :-) I am not an electronics expert, but ive been around the block many times. all the major electrical work like the grounding rod and the run from the mains was done by a licensed electrcian as rqd by local code ![]() different guy just to make sure it wasnt something fsked up with the first guys wiring Good. I have no doubt your grounding is good. BTW - do you have pictures of your outside tank setup? I am interested in seeing it if you have them available. |