A Fishkeeping forum. FishKeepingBanter.com

If this is your first visit, be sure to check out the FAQ by clicking the link above. You may have to register before you can post: click the register link above to proceed. To start viewing messages, select the forum that you want to visit from the selection below.

Go Back   Home » FishKeepingBanter.com forum » rec.aquaria.marine » Reefs
Site Map Home Authors List Search Today's Posts Mark Forums Read Web Partners

Electrical Question



 
 
Thread Tools Display Modes
  #1  
Old April 13th 04, 08:05 AM
Travis A.
external usenet poster
 
Posts: n/a
Default Electrical Question

I am trying to figure out if need to add more outlets around my tank. In
the future I want to upgrade to MH lighting and was not sure if my current
set up would be safe adding Mh also.

This is what I have now and maybe you could answer my question.

I am currently using 2 outlets, both are on the same circuit. Icecap 660
with 440 watts of VHO lighting, mag 9.5 & 7 for tank circulation & skimmer,
200 watt heater, 2 maxi jet power heads and fan in canopy, & 2 other outlets
for my calcium reactor. In the future I will probably upgrade to 2 175 watt
MH with VHO. My question is would I need to add another outlet or 2 from the
breaker box to run all of this safely or go to a higher amp breaker.

Thanks
Travis


  #2  
Old April 13th 04, 09:17 AM
Richard Reynolds
external usenet poster
 
Posts: n/a
Default Electrical Question

what size breaker is your setup on now?
how many other outlets are on it?
whats the wire size for the run?
if you endup running a larger run (probilby not) its gona be cheaper/easier/more
upgradeable to run a heavy guage high amp circuit between the main breaker and a new
junction box near the tank. regardless the junction box can be good for giving extra
outlets which IME you always need more of. more so if you use things that run off of plug
in power transformers which seem to take up 3 outlets.

dont just go to a higher amp breaker the wires should be large enough to handle the load.

--
Richard Reynolds



  #3  
Old April 15th 04, 01:18 AM
J Codling
external usenet poster
 
Posts: n/a
Default Electrical Question

If you have a 20A circuit with #12 wire with only these receptacles
connected to it you are allowed:

..8*20*120 watts on that circuit = 1920W

If you have #14 wire then you are allowed .8*15*120 watts = 1440W

Too be conservative maybe use 1500W PER CIRCUIT for 20A and 1200W PER
CIRCUIT for 15A. That isn't per plug, but per circuit. So you need to
verify how the receptacles are wired. Make sure they aren't connected
together on the same breaker by turning off the breaker and make sure those
are the only receptacles that are turned off. . THat's easy to check and
then make sure nothing else is connected to those circuits, otherwise that
takes away from your 1500W. Hope that helps..

Jim




"Richard Reynolds" wrote in message
news:ImNec.83$fq4.67@lakeread05...
what size breaker is your setup on now?
how many other outlets are on it?
whats the wire size for the run?
if you endup running a larger run (probilby not) its gona be

cheaper/easier/more
upgradeable to run a heavy guage high amp circuit between the main breaker

and a new
junction box near the tank. regardless the junction box can be good for

giving extra
outlets which IME you always need more of. more so if you use things that

run off of plug
in power transformers which seem to take up 3 outlets.

dont just go to a higher amp breaker the wires should be large enough to

handle the load.

--
Richard Reynolds





  #4  
Old April 15th 04, 02:30 AM
Steve Sells
external usenet poster
 
Posts: n/a
Default Electrical Question

you forgot the 80% rating of max load as per NEC.

IF you are running a circuit at 100%, its asking for trouble. As an
Electrician we NEVER allow a 20A to get over 1800, and as you said 1600 is
normal. 1200 for 15a.

Steve


"J Codling" wrote in message
ink.net...
If you have a 20A circuit with #12 wire with only these receptacles
connected to it you are allowed:

.8*20*120 watts on that circuit = 1920W

If you have #14 wire then you are allowed .8*15*120 watts = 1440W

Too be conservative maybe use 1500W PER CIRCUIT for 20A and 1200W PER
CIRCUIT for 15A. That isn't per plug, but per circuit. So you need to
verify how the receptacles are wired. Make sure they aren't connected
together on the same breaker by turning off the breaker and make sure

those
are the only receptacles that are turned off. . THat's easy to check and
then make sure nothing else is connected to those circuits, otherwise that
takes away from your 1500W. Hope that helps..

Jim




"Richard Reynolds" wrote in message
news:ImNec.83$fq4.67@lakeread05...
what size breaker is your setup on now?
how many other outlets are on it?
whats the wire size for the run?
if you endup running a larger run (probilby not) its gona be

cheaper/easier/more
upgradeable to run a heavy guage high amp circuit between the main

breaker
and a new
junction box near the tank. regardless the junction box can be good for

giving extra
outlets which IME you always need more of. more so if you use things

that
run off of plug
in power transformers which seem to take up 3 outlets.

dont just go to a higher amp breaker the wires should be large enough to

handle the load.

--
Richard Reynolds







  #5  
Old April 15th 04, 02:57 AM
J Codling
external usenet poster
 
Posts: n/a
Default Electrical Question

That's why I multiplied it by .8!




"Steve Sells" wrote in message
ink.net...
you forgot the 80% rating of max load as per NEC.

IF you are running a circuit at 100%, its asking for trouble. As an
Electrician we NEVER allow a 20A to get over 1800, and as you said 1600

is
normal. 1200 for 15a.

Steve


"J Codling" wrote in message
ink.net...
If you have a 20A circuit with #12 wire with only these receptacles
connected to it you are allowed:

.8*20*120 watts on that circuit = 1920W

If you have #14 wire then you are allowed .8*15*120 watts = 1440W

Too be conservative maybe use 1500W PER CIRCUIT for 20A and 1200W PER
CIRCUIT for 15A. That isn't per plug, but per circuit. So you need to
verify how the receptacles are wired. Make sure they aren't connected
together on the same breaker by turning off the breaker and make sure

those
are the only receptacles that are turned off. . THat's easy to check

and
then make sure nothing else is connected to those circuits, otherwise

that
takes away from your 1500W. Hope that helps..

Jim




"Richard Reynolds" wrote in message
news:ImNec.83$fq4.67@lakeread05...
what size breaker is your setup on now?
how many other outlets are on it?
whats the wire size for the run?
if you endup running a larger run (probilby not) its gona be

cheaper/easier/more
upgradeable to run a heavy guage high amp circuit between the main

breaker
and a new
junction box near the tank. regardless the junction box can be good

for
giving extra
outlets which IME you always need more of. more so if you use things

that
run off of plug
in power transformers which seem to take up 3 outlets.

dont just go to a higher amp breaker the wires should be large enough

to
handle the load.

--
Richard Reynolds









  #6  
Old April 15th 04, 03:03 AM
tech27
external usenet poster
 
Posts: n/a
Default Electrical Question



"Steve Sells" wrote in message
ink.net...
you forgot the 80% rating of max load as per NEC.


That's why he has .8 or 80% in the calculation.

IF you are running a circuit at 100%, its asking for trouble. As an
Electrician we NEVER allow a 20A to get over 1800, and as you said 1600

is
normal. 1200 for 15a.


The simple and extra safe way is to calculate amps x 100 volts for a 120
service.
This gives you 1000 watts for a 15 amp circuit.
The same calculation gives you 2000 watts max for a 20 amp run.

Why do you say that you never want it to go over 1800? That's only 75%. If
you have the proper gge wire and receptacles, what's the problem?



Steve


"J Codling" wrote in message
ink.net...
If you have a 20A circuit with #12 wire with only these receptacles
connected to it you are allowed:

.8*20*120 watts on that circuit = 1920W

If you have #14 wire then you are allowed .8*15*120 watts = 1440W

Too be conservative maybe use 1500W PER CIRCUIT for 20A and 1200W PER
CIRCUIT for 15A. That isn't per plug, but per circuit. So you need to
verify how the receptacles are wired. Make sure they aren't connected
together on the same breaker by turning off the breaker and make sure

those
are the only receptacles that are turned off. . THat's easy to check

and
then make sure nothing else is connected to those circuits, otherwise

that
takes away from your 1500W. Hope that helps..

Jim




"Richard Reynolds" wrote in message
news:ImNec.83$fq4.67@lakeread05...
what size breaker is your setup on now?
how many other outlets are on it?
whats the wire size for the run?
if you endup running a larger run (probilby not) its gona be

cheaper/easier/more
upgradeable to run a heavy guage high amp circuit between the main

breaker
and a new
junction box near the tank. regardless the junction box can be good

for
giving extra
outlets which IME you always need more of. more so if you use things

that
run off of plug
in power transformers which seem to take up 3 outlets.

dont just go to a higher amp breaker the wires should be large enough

to
handle the load.

--
Richard Reynolds









  #7  
Old April 15th 04, 06:25 PM
Steve Sells
external usenet poster
 
Posts: n/a
Default Electrical Question



That's why he has .8 or 80% in the calculation.


I miss read that.he did include it. My bad.

snip

Why do you say that you never want it to go over 1800? That's only 75%. If
you have the proper gge wire and receptacles, what's the problem?



Voltage drop from the distance needs to be figured in for wire gauge also.
So does Ambient temperature. example 12 gauge wire is fine for most lines,
but if I am running a line to the back yard, the voltage drop may make it
only safe for 9 or10 amps, so we may have to use 10 or even 8 guage to allow
the full power we need. and a hot location for wiring lowers the amps that
can pass safely.

We use round numbers for most applications for "Off the cuff " figures. I
should have used the calculations, like when we do a blue print, with all
the voltage drop, resistance for ambient temperatures, Wire Jacket type, and
the load also figured in.

Since the code says Not over 80% we add a little to cover being too lazy to
re-calculate every run on a job site, the round numbers, tell us if we are
safe, IF it is "over" the round numbers we use... then we get out the code
book, and a calculator and then double check the full formula before
installing the lines.

Its like when we drive a car, we know about how fast we are driving, but
when we see a cop, we LOOK at the speedometer, to make sure we are not in
trouble. I need to be clearer when I post.

Sorry

Steve


  #8  
Old April 15th 04, 11:34 PM
Richard Reynolds
external usenet poster
 
Posts: n/a
Default Electrical Question

Its like when we drive a car, we know about how fast we are driving, but
when we see a cop, we LOOK at the speedometer, to make sure we are not in
trouble.


I know and i usually have to slow down like 30-40mph also they always frown on 95mph in
the 65 zones


--
Richard Reynolds





  #9  
Old April 16th 04, 03:47 AM
tech27
external usenet poster
 
Posts: n/a
Default Electrical Question

No need to apologize, I was just curious.

I realize that runs and temp come into play, but I think you would have to
have a pretty long run in a very hot environment to cause any problems IF
you are using all appropriate materials for a 20 amp run.

We have one installation (I do sound/video and lighting-the big power draw)
and we put in our own 800 amp xformer and ran feeds up to the location. Then
we distributed it from a subpanel on Socapex as required. This setup should
handle most aquarium needs. Probably all of Sea World. (-;


"Steve Sells" wrote in message
ink.net...


That's why he has .8 or 80% in the calculation.


I miss read that.he did include it. My bad.

snip

Why do you say that you never want it to go over 1800? That's only 75%.

If
you have the proper gge wire and receptacles, what's the problem?



Voltage drop from the distance needs to be figured in for wire gauge also.
So does Ambient temperature. example 12 gauge wire is fine for most

lines,
but if I am running a line to the back yard, the voltage drop may make it
only safe for 9 or10 amps, so we may have to use 10 or even 8 guage to

allow
the full power we need. and a hot location for wiring lowers the amps

that
can pass safely.

We use round numbers for most applications for "Off the cuff " figures.

I
should have used the calculations, like when we do a blue print, with all
the voltage drop, resistance for ambient temperatures, Wire Jacket type,

and
the load also figured in.

Since the code says Not over 80% we add a little to cover being too lazy

to
re-calculate every run on a job site, the round numbers, tell us if we are
safe, IF it is "over" the round numbers we use... then we get out the

code
book, and a calculator and then double check the full formula before
installing the lines.

Its like when we drive a car, we know about how fast we are driving, but
when we see a cop, we LOOK at the speedometer, to make sure we are not in
trouble. I need to be clearer when I post.

Sorry

Steve




  #10  
Old April 17th 04, 03:11 AM
Steve Sells
external usenet poster
 
Posts: n/a
Default Electrical Question

I have used the Leprechaun controllers with remote dimmers and big Pars...
but usually I just play bass...

Steve

"tech27"
No need to apologize, I was just curious.

I realize that runs and temp come into play, but I think you would have to
have a pretty long run in a very hot environment to cause any problems IF
you are using all appropriate materials for a 20 amp run.

We have one installation (I do sound/video and lighting-the big power

draw)
and we put in our own 800 amp xformer and ran feeds up to the location.

Then
we distributed it from a subpanel on Socapex as required. This setup

should
handle most aquarium needs. Probably all of Sea World. (-;



 




Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical Question Travis A. General 3 May 13th 04 05:44 AM
Question about copper Marco Qualizza Reefs 5 April 11th 04 08:43 PM
DIY Electrical question Lawrence General 9 March 23rd 04 08:43 PM
Bioload Question Kelley Reefs 1 February 25th 04 12:06 PM
I need a very simple answer to a lighting and filter question. Ben General 8 July 26th 03 07:12 AM


All times are GMT +1. The time now is 11:37 AM.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
Copyright ©2004-2025 FishKeepingBanter.com.
The comments are property of their posters.